Il manuale dice :
...'Control in the heating mode
During the heating mode, the room temperature or the temperature of the sucked in heating air is constantly measured.
If the temperature is higher than the temperature selected on the control element, the heater starts to regulate its output.
There are 4 control stages so that the outflow of heat produced by the heater can be adjusted finely to the heating requirements.
Fan speed and fuel quantity correspond to the particular control stage.
If the set temperature is still exceeded in the smallest control stage, the heater goes to the “OFF” stage with the fan running on for approx. 4 minutes to cool off.
The fan then continues running at minimum speed (circulation mode) until the restart or is switched off (fresh air mode with external temperature sensor).'...
Tradotto solo cio' che interessa con fra parentesi note di chiarimento :
...'se la temperatura impostata viene superata nello stadio di minimo controllo (la piu' bassa potenza) il riscaldatore si spegne con il ventilatore in azione per 4 minuti per raffreddare. Il ventilatore continua poi a funzionare alla minima velocita' fino alla riaccensione (da parte del termostato) o allo spegnimento (manuale)'...
Quindi e' normale che si comporti in quel modo. Io ho un altro modello ma il comportamento e' uguale.
|
|